International Journals June-Seok Lee and Kyo-Beum Lee, "Open-Circuit Fault Tolerant Control for Outer Switches of Three-Level Rectifiers in Wind Turbine Systems," IEEE Transactions on Power Electronics, vol. 31, no. 5, pp. 3806–3815, May 2016. -SCI
2016
본문
A three-level converter is used as the power converters of wind turbine systems because of their advantages such as low-current
total harmonic distortion, high efficiency, and low collector-emitter voltage. Interior permanent magnet synchronous generators
(IPMSGs) have been chosen as the generator in wind turbine systems owing to their advantages of size and efficiency. In wind
turbine systems consisting of the three-level converter and the IPMSG, fault-tolerant controls for an open-circuit fault of switches
should be implemented to improve reliability. This paper focuses on the open-circuit fault of outer switches (Sx1 and Sx4) in three-
level rectifiers(both neutral-point clamped and T-type) that are connected to the IPMSG. In addition, the effects of Sx1 and Sx4 open-
circuit faults are analyzed, and based on this analysis, a tolerant control is proposed. The proposed tolerant control maintains
normal operation with sinusoidal currents under the open-circuit fault of outer switches by adding a compensation value to the
reference voltages. The effectiveness and performance of the proposed tolerant control are verified by simulation and experiment.